i was going to use a pid from auberins with the ssr output, im wanting to know what size ssr for 4 X 3100 elements or is this possible with a 60 amp breaker and what other things would i need to get like and does any one have this type of set up that has pics of the diagram or the box wired up thanks alot
(4) 3100 watt elements would draw about 52 amps. (4X3100/240) I would go with a 75 amp ssr and a good heat sink. This is about the limit for your 60 amp circuit.

If you're looking to run all elements simultaneously, then there is nothing special about doing this. Look up some of the wiring diagrams people have posted here.