Default Wiring Question - I'd appreciate any help

I built an oven roughly 3 1/2 ' x 4 ' x 5' with three 3100 watt heating coils. I'm having trouble getting the contactor to work correctly. I have 240 60 amp circuit 4 wire. I have a TET 612 PID. I have a 75 amp terminal block and a Fasco 3 pull 60 amp magnetic contactor. I used th schematics attached and wired it identically. The only thing I did different was adding switches before and after the PID. The problem I'm having is when we flip the switch to send the power into the coil of the contactor it burned up the coil of the contactor. I'm only using 2 of the pulls on the contactor. I'm using 6 gage wire from the 120 vac lines to the contactor and from the contactor to the terminal block. Everything else is 12 gage wire. Before I changed to this I used a 90 amp SSR wire with a different schematic and it burned up the SSR so I switched to a contactor with this schematic. Any help with this situation will be greatly appreciated. I know I'm close but don't know what I'm doing wrong.
Attached Files
File Type: pdf schematic.pdf (12.4 KB, 43 views)
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #2 (permalink)  
Old 10-17-2009, 01:24 PM
Experienced Metal Finisher
 
Join Date: May 2008
Posts: 305
Grumple is on a distinguished road
Default Re: Wiring Question - I'd appreciate any help

Sounds like you are wiring the coil with 2 hots instead of a hot and a neutral. This is fine for a 240 volt coil but not so fine for a 120v coil.
__________________
Grumple
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #3 (permalink)  
Old 10-17-2009, 01:37 PM
Metal Finishing Guru
 
Join Date: Jul 2006
Posts: 618
ed_denu will become famous soon enoughed_denu will become famous soon enough
Default Re: Wiring Question - I'd appreciate any help

I think Dave is correct, make sure that the contactor coil voltage is correct for the voltage you supplied. If you wired it per the schematic is it possible the coil was a 24 volt, that's a common voltage for contactors?

Last edited by ed_denu; 10-17-2009 at 01:48 PM.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #4 (permalink)  
Old 10-17-2009, 02:22 PM
Newbie
 
Join Date: Aug 2009
Posts: 6
snowhoundxp is on a distinguished road
Default Re: Wiring Question - I'd appreciate any help

Thanks for responding. The coil I'm using is a 24V, 50/60 HZ. I wired it just like the schematic so I have one hot and one neutral. Is that not correct? The hot is coming off the PID. The neutral is coming off the block.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #5 (permalink)  
Old 10-17-2009, 09:39 PM
Metal Finishing Guru
 
Join Date: Jul 2006
Posts: 618
ed_denu will become famous soon enoughed_denu will become famous soon enough
Default Re: Wiring Question - I'd appreciate any help

The schematic is drawn for a 120 volt coil. You cannot put 120 volts on a 24 volt coil and have it work. You need to acquire a contactor of the appropriate amperage with a 120 volt coil.

The 24V coil/contactor would only work if you added a transformer to reduce the voltage from the pid relay to 24 volts. Since you stated that the contactor coil is already burnt, I would just get a different contactor.

Last edited by ed_denu; 10-17-2009 at 09:54 PM.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #6 (permalink)  
Old 10-17-2009, 10:07 PM
Experienced Metal Finisher
 
Join Date: May 2008
Posts: 305
Grumple is on a distinguished road
Default Re: Wiring Question - I'd appreciate any help

The old 24 volt coil trick heh? (As Maxwell Smart would say). Lots of industrial control panels use 24 volt coils and like Ed said, they use a step-down transformer for the control voltage. You could add a transformer but that is more money and not really necessary. You could use a 120 or 240 volt coil on your new contactor but I would recommend a 120v coil or you will have some other minor details with DPDT switches to work out...
Grump

http://cgi.ebay.com/NEW-CONTACTOR-CN...item5ad130db0b
__________________
Grumple

Last edited by Grumple; 10-17-2009 at 10:12 PM.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #7 (permalink)  
Old 10-17-2009, 10:35 PM
Newbie
 
Join Date: Aug 2009
Posts: 6
snowhoundxp is on a distinguished road
Default Re: Wiring Question - I'd appreciate any help

Thanks for the imput now i know what to do.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wiring question simplytodd Oven Building Forum 10 01-20-2009 06:53 PM
another wiring question 97ramsport Oven Building Forum 2 08-12-2008 02:13 PM
Yet another wiring question... 97Dually Oven Building Forum 8 12-04-2007 12:52 AM
Wiring question ed_denu Oven Building Forum 5 08-10-2007 09:14 PM