240 volt circuits if they are 3 wire are (2) 120 volt legs and a ground. The ground is for safety considerations and the circuit would be complete and functional without the 3rd wire. A (4) wire 240 volt circuit has (2) hot legs, a ground and a neutral. The neutral allows for the circuit to provide a 120 volt source along with a 240 volt capability.

A 3 wire 240 volt circuit is not meant to supply a 120 volt source, while a (4) wire 240 volt circuit can supply both 240 volts and a 120 volt source. Typically for a (3) wire circuit, if romex is used, the black wire is hot, the white wire is marked black with either a marker pen or black electrical tape, and the green or bare is ground. With (4) wire cable, the hots are red and black, the ground is bare or sometimes green, while the 4th wire can be white, or another color. The NEC in most cases does not specify wire colors except for larger conductor sizes and 3 phase power.

Scott, I think you are referring to older dryer setups that sometimes used the ground as a neutral, but this is an exception to the rule and not the norm.

Last edited by ed_denu; 10-31-2009 at 01:45 PM.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #12 (permalink)  
Old 10-31-2009, 01:28 PM
philipd's Avatar
Newbie
 
Join Date: Sep 2008
Posts: 12
philipd is on a distinguished road
Default Re: More wiring???

Quote:
Originally Posted by SCOTTRODS View Post
It's not a dumb question.... It is apparent there's not much electrical knowledge in your life though. That's nothing to be ashamed of at all.
Yeah, it is apparent. Most of my electrical training as been from "This Old House", "Hometime", and other shows on HGTV. Also to some extent from what I have read on the internet and gathered from DIY books. One drawback to this is that I have learned HOW to wire something but not WHY. So I guess my question should be: how come a 240v circuit doesn't require a neutral wire? I understand from Ed's post (thanks Ed) that a neutral is required in a modern home but what I don't understand is why it will work without a neutral.

If you look at the diagram in the original post you will see one leg (colored brown) goes to the SSR and then four wires exit, one to each of four elements. The other leg (colored black) exit the terminal strip and goes to the other side of each element. No neutral.

This really isn't important. I know it will work -- I just don't know why.
__________________
'09 Kawasaki 500 LTD
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #13 (permalink)  
Old 10-31-2009, 01:29 PM
Metal Finishing Guru
 
Join Date: Jul 2006
Posts: 618
ed_denu will become famous soon enoughed_denu will become famous soon enough
Default Re: More wiring???

Quote:
Originally Posted by philipd View Post
Dumb question here: why doesn't a 240 circuit have a neutral? Does one leg act as a neutral for the other leg?
It's not a dumb question and you have the right idea. In a 240 volt single phase circuit the sine waves of the (2) hot legs are each 180 degrees apart and serve as a return path for the other to complete the circuit. When one conductor is positive, the other is negative, so the circuit is complete. A dedicated 'neutral' is not required. If the sine waves weren't 180 degrees apart, there would be no voltage present. The same as if you ran a (2) wire circuit with both feeds coming from the same hot leg, you would see 0 volts.

In 120 volt circuits, one sine wave(providing 120 volts) is used along with a neutral to complete a circuit. As the AC sine wave alternates between positive and negative, the circuit is positive 50% of the time, negative 50% of the time. This occurs 60 times a sec, hence the designation 60 hz.

Last edited by ed_denu; 10-31-2009 at 01:49 PM.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #14 (permalink)  
Old 10-31-2009, 01:43 PM
philipd's Avatar
Newbie
 
Join Date: Sep 2008
Posts: 12
philipd is on a distinguished road
Default Re: More wiring???

Thanks Ed!

That makes perfect sense! As one leg goes above neutral the other leg is going below neutral. Don't know why I didn't think of it.

Well, I do know why I didn't think of it. I didn't know that the legs were 180° apart.

I love learning new stuff.
__________________
'09 Kawasaki 500 LTD

Last edited by philipd; 10-31-2009 at 01:52 PM.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #15 (permalink)  
Old 10-31-2009, 01:44 PM
Metal Finishing Guru
 
Join Date: Jul 2008
Location: Garland, TEXAS
Posts: 524
SCOTTRODS is an unknown quantity at this point
Default Re: More wiring???

Quote:
Originally Posted by ed_denu View Post
Scott, I think you are referring to older dryer setups that sometimes used the ground as a neutral, but this was an exception to the rule and not the norm.
Yes,... I use a dryer circuit on my oven.... At least it's wired like the one on my dryer....
__________________


See photos of my work at the following link
http://s244.photobucket.com/albums/gg6/terrellster/
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #16 (permalink)  
Old 10-31-2009, 02:22 PM
Metal Finishing Guru
 
Join Date: Jul 2006
Posts: 618
ed_denu will become famous soon enoughed_denu will become famous soon enough
Default Re: More wiring???

Quote:
Originally Posted by SCOTTRODS View Post
Yes,... I use a dryer circuit on my oven.... At least it's wired like the one on my dryer....
Scott, If you are using a 3 wire circuit on your oven you should seriously consider converting it to a 4 wire circuit. 120 volt devices will place current on the ground. This can create a dangerous situation. The pid, lights, fan should have a dedicated neutral and the ground should be for short circuit, safety considerations only.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
NEED HELP With Wiring snowhoundxp Oven Building Forum 3 08-26-2009 11:32 AM
Wiring goincrzy Oven Building Forum 12 02-03-2009 08:59 PM
need to buy wiring?? cjlee Oven Building Forum 1 09-13-2006 02:38 PM
Wiring help now??? Evolved Oven Building Forum 5 07-06-2006 10:14 PM
Wiring 101 :) hvac36 Powder Coating Questions 3 12-23-2004 04:58 PM


All times are GMT -4. The time now is 01:55 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0
Copyright © Caswell Inc.