Each leg is going to pull 50 amps (at 240) , common mistake is to think a 50 amp device draws 25 amps per leg. Your SSR is going to see 50 amps on the one leg. Why are you not breaking both legs with the SSR? Maybe it's an SSR thing? I refuse to use them, I want something that 99.9% of the time is going to fail in the "open" position, like a contactor, having an SSR fail and stay closed would keep me awake at night.
The neutral and ground only terminate in the same spot if it's in the "primary means of disconnect". What do you mean that L1 and L2 are on separate breakers? They MUST be on one 2 pole breaker.