I think there is something wrong with the set-up/wiring. The upper display is the present value or current temperature reading. The lower is the set value. Check the polarity of the thermocouple wire leads ataching to the pid. They should be attached to terminals 9 & 10, with 9 being the + side.
Also you need to check that you have the correct thermocouple defined in the pid. The default tc for the tet612 is PT10, but the more common tc's used are the K type, so the INTY parameter needs to be changed to 'K'. Look at section 4 Parameter Setting for instructions on how to change the INTY parameter.
You also need to make sure OUTY is set to the correct ssr or contactor usage and that RD is set to heating and CORF is set to fahrenheit.