That's correct, you are the winner(but you still need to build the oven and controls).
OK installing a 60 Amp CB for my 240v Oven outlet. You want to keep it at 80% so I take 48A x 240v = 11500 Watts.
Is that correct? I can use 4 2880 Watt elements.
Do I win?!![]()
That's correct, you are the winner(but you still need to build the oven and controls).
That may not work well unless you are going to use multiple controls from the ovens. Even ovens with self cleaning cycles typically only use 2 elements at a time. Attempting to use 4 is going to surely create an overload on the wiring, and whatever is used to control the element switching such as a contactor.