Default Ok, I have some serious concerns about venting.

Sorry I should have started my own new post but I posted in this thread instead. ( An Idea -building An Oven From Cement Board )

The oven is 6x4x3 and is constructed of steel studs and durock.

Heat is supplied by a 175k-350k LP Forced air unit.

Now to my question('s), Do I need a vent of some sort on this unit?

I wanted to use Electric elements but I know nothing about electrical wiring, amp, voltage etc.

I may use "loosely knitted" rope for a really snug seal, is fiberglass an acceptable form of material? http://www.mcmaster.com , rope seal , 8818K45

I'm stressing because, after all it is PROPANE..!!

ANY info would be great, Thanks a lot.
Reply With Quote
  #2 (permalink)  
Old 12-14-2005, 09:33 PM
bluegiller's Avatar
Newbie
 
Join Date: Oct 2005
Posts: 13
bluegiller is on a distinguished road
Default Re: Ok, I have some serious concerns about venting.

almost 40 views and no one willing to jump in?

Im in the middle of another test run with a 2 foot extension tube and i put 2 pieces of expanded metal near the inlet inside of the oven to deflect some air but it still seems to powerfull.
Reply With Quote
  #3 (permalink)  
Old 12-14-2005, 10:17 PM
pickleboy's Avatar
Metal Finishing Guru
 
Join Date: Feb 2005
Location: belleville michigan
Posts: 635
pickleboy is just really nicepickleboy is just really nicepickleboy is just really nicepickleboy is just really nice
Default Re: Ok, I have some serious concerns about venting.

Quote:
Originally Posted by bluegiller
almost 40 views and no one willing to jump in?

Im in the middle of another test run with a 2 foot extension tube and i put 2 pieces of expanded metal near the inlet inside of the oven to deflect some air but it still seems to powerfull.
i will try to help but since i have not built my own oven i may be of little help. as for the vent yes you should have some sort of vent. i would suggest that you make it a damper type of vent. this will help you regulate the temp without having to start and stop the heater. as for the air flow it may have to have some sort of solid baffle system that will difuse the air so as to not blow the powder off the part.
"I'm stressing because, after all it is PROPANE"
as for the worries on propane i think it should be safe as long as you are very careful with the bottle placement. propane generally burns about 90-98% clean, so fume problems should be minimal. hope this helps some bro.
__________________
when in doubt polish it out/ why replace it when you can refinish it
G2 Polishing and Powdercoating
Reply With Quote
  #4 (permalink)  
Old 12-14-2005, 10:34 PM
bluegiller's Avatar
Newbie
 
Join Date: Oct 2005
Posts: 13
bluegiller is on a distinguished road
Default Re: Ok, I have some serious concerns about venting.

Thanks a lot.

I'm not even getting close!! I need another 100 degrees and it just isn't happening, this is so aggrevating.

I believe there is to much airflow kicking back to the heater and the flame is going over the back side of the heater and that is when it cuts/turns off.

I have no clue what a solid baffle or a damper is but I will goggle it and hope to find some info out.

I read in other threads where people talked about the dampers but Im just not familar with them.

I'm so frustrated its unreal..

I will go to electric if I cant get this propane to work, I just really needed to get the frame done before christmas.

Thanks for the reply
Reply With Quote
  #5 (permalink)  
Old 12-14-2005, 11:32 PM
pickleboy's Avatar
Metal Finishing Guru
 
Join Date: Feb 2005
Location: belleville michigan
Posts: 635
pickleboy is just really nicepickleboy is just really nicepickleboy is just really nicepickleboy is just really nice
Default Re: Ok, I have some serious concerns about venting.

damper would be a tube with a disc in it that will open to full flow or close all the way across the tube to close it. like a butterfly valve if you are familar with them. or similar to a fireplace chimney flue. as for solid baffles you may need to build some sort of plates alternating diagonoly from left to right then right to left in kind of a stairstep stagger. this will slow down the flow of air to the box but should stop most of the backpressure to the heater. if all else fails cut a small v notch in the end of the extension pipe from the heater to the box. this will allow some of the airflow to escape and also relieve backpressure. if i could draw on here i would since my explaining is not the best. if you are getting backpressure on the discharge end of that heater it will cause an overtemp and shutdown. if you need help shoot me a pm and i will give you my phone # so you can call.
__________________
when in doubt polish it out/ why replace it when you can refinish it
G2 Polishing and Powdercoating
Reply With Quote
  #6 (permalink)  
Old 12-14-2005, 11:34 PM
sswee's Avatar
Moderator
 
Join Date: Nov 2004
Location: close to Austin, Texas
Posts: 1,201
sswee is a jewel in the roughsswee is a jewel in the roughsswee is a jewel in the roughsswee is a jewel in the rough
Default Re: Ok, I have some serious concerns about venting.

The air that the heater puts out is pressurizing you oven and backpressuring into the heater causing the thermal overheat switch to shut down the heater. That type of heater has the switch as a safety feature to keep from burning the heater up.
A damper in that respect is going to be a hole probably equal in size to the inlet but located in the top of the opposite side and will have a piece that can be rotated to cover the vent hole in any amount desired. Dampers are commonly used on BBQ pit stacks as a plate that rotates over the top of the smoke stack or fireplaces as a disc inside the smoke pipe that can be rotated to restrict or dampen the heat flow out of the pipe.

I understand your hesitance in delving into the electrical way if your not familiar with it but due to the safety issues, you aren't going to get the assistance as you will going electric. I hope you understand. SS
Reply With Quote
  #7 (permalink)  
Old 12-14-2005, 11:45 PM
pickleboy's Avatar
Metal Finishing Guru
 
Join Date: Feb 2005
Location: belleville michigan
Posts: 635
pickleboy is just really nicepickleboy is just really nicepickleboy is just really nicepickleboy is just really nice
Default Re: Ok, I have some serious concerns about venting.

Quote:
Originally Posted by sswee
but due to the safety issues, you aren't going to get the assistance as you will going electric. I hope you understand. SS
sswee is right on this, gas heat source is not the safest way to go. it has been done by quite a few here and elsewhere. the only way gas heat is truly safe is if in a sealed burner box and air is forced around to draw the heat off said box, like a heat exchanger in your house furnace. also keep in mind that gas heat (natural or propane) being combustion in nature will produce water vapor as a byproduct of the burn. that said if your heater blows right in your oven box it can contaminate the pc job as it cures. not a fact it will happen but could.
__________________
when in doubt polish it out/ why replace it when you can refinish it
G2 Polishing and Powdercoating
Reply With Quote
  #8 (permalink)  
Old 12-14-2005, 11:45 PM
bluegiller's Avatar
Newbie
 
Join Date: Oct 2005
Posts: 13
bluegiller is on a distinguished road
Default Re: Ok, I have some serious concerns about venting.

Thanks guys, Well I just done removing 2 of the 4 blades on the heater fan to try and slow the air flow, needless to say the backpressure is still there...

The damper idea must work but just seems like it would let to much heat out
(trust me I understand you can/do meter the flow out.)

As far as the homemade baffles your speaking of I'm a bit lost so will take you up on you phone call offer, pm on its way.

Thanks fellas.
Reply With Quote
  #9 (permalink)  
Old 12-15-2005, 12:18 AM
hvac36's Avatar
Moderator
 
Join Date: Jul 2004
Location: New Milford, PA
Posts: 219
hvac36 will become famous soon enough
Send a message via AIM to hvac36
Default Re: Ok, I have some serious concerns about venting.

Quote:
Originally Posted by bluegiller
Thanks guys, Well I just done removing 2 of the 4 blades on the heater fan to try and slow the air flow, needless to say the backpressure is still there...

The damper idea must work but just seems like it would let to much heat out
(trust me I understand you can/do meter the flow out.)

As far as the homemade baffles your speaking of I'm a bit lost so will take you up on you phone call offer, pm on its way.

Thanks fellas.
Ok here is the deal, unless you get the flame out of the Oven and place it in a SEALED heat exchanger that oven is UNSAFE!! Open Flame and Blowing Powder DO NOT MIX!!! Well they do but the mix is NOT a good MIX.
Either buy a Gas oven from a company that makes them for this use or Build and electric oven please..
Need help wiring it I will be more then happy to talk you thru it or draw you and image or snap a Image of mine...
Lets be safe folks...

Jim S....
__________________
Jim Shuster
www.backyardpowdercoating.com Sold.....
www.chrissys68mustang.com Hobbie
www.photogserver.net Web Hosting.
Reply With Quote
  #10 (permalink)  
Old 12-15-2005, 01:30 AM
bluegiller's Avatar
Newbie
 
Join Date: Oct 2005
Posts: 13
bluegiller is on a distinguished road
Default Re: Ok, I have some serious concerns about venting.

Quote:
Originally Posted by hvac36
Ok here is the deal, unless you get the flame out of the Oven and place it in a SEALED heat exchanger that oven is UNSAFE!! Open Flame and Blowing Powder DO NOT MIX!!! Well they do but the mix is NOT a good MIX.
Either buy a Gas oven from a company that makes them for this use or Build and electric oven please..
Need help wiring it I will be more then happy to talk you thru it or draw you and image or snap a Image of mine...
Lets be safe folks...

Jim S....
Thanks for suggestion, It certainly looks like I'll be going electric with this oven.

I should be able to get a pretty penny for this heater that should cover any expense all the electronics will cost.

What about Radiant heaters??

Thanks again
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

Similar Threads
Thread Thread Starter Forum Replies Last Post
Oven venting? viper56 Powder Coating Questions 2 12-05-2004 10:54 PM
venting? csaddler Oven Building Forum 4 01-20-2004 11:03 AM


All times are GMT -4. The time now is 03:32 PM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.2.0 RC4
Copyright © Caswell Inc.