Thanks to this board I've got my oven finished up, and enclosed ( 4x4x8 ). All I need to do is wire the leads going to the elements up. This is where I'm confused/concerned. Here are my questions.
Can I use the thermostat out of a normal house oven, and run it into the contactor in the link below and be fine? http://cgi.ebay.com/HONEYWELL-R8234B...QQcmdZViewItem I'm running 3 - 3300 watt elements 220v single phase If not what will I need, and please include part numbers. Thanks in advance to anyone who will shed a little light for me. Last edited by itsallgood; 12-26-2006 at 03:10 AM. |
|
||||
|
OK here we go you got 3X3300 = 6600*220 = 45 amps. 220 single phase = 2 poles. This is the contactor you need and yes you can use a house oven thermostate with it. It's good for 50 amps res. you only have 45 amps. And it has a 120 volt coil witch you all ready have the power for with your 220v power supply. It's realy not that bad if you need help give me a PM and we can talk on the phone it's a lot easyer. I've gotten a few dudes through it that did't have a clue LOL... Good luck and Merry Christmas
http://www.famousparts.com/c25bnf240aco.html http://www.powdercoatoven.4t.com/Index.html ![]()
|
|
|||
|
|
|
|||
|
I'm also gathering info to build a 4x4x8 oven, can you explain what the "contactor" and the "120 volt coil " is for?
I have 2 complete house ovens and was wondering if it would be easier just to strip them down and just reuse the controls, elements and associated parts as they are currently wired? Meaning I would have to temp controls for the one larger oven. |
|
|||
|
|
|
||||
|
You got it dude... just run the coil circuit from one side of your 220v oven feed. Run the hot through the thermostat (like a light switch) and then to the coil and run the neutral straight to the coil on the contactor. The thermostat tells the coil when to energize to complete the 220v circuit to the elements and vise versa. I talk to much, later.....
|
|
|||
|
Quote:
|
|
||||
|
In a house oven your only running one element at a time. You need a contactor that can handle the amps of more than one element running at a time. 3300watt * 220v = 15amp now times that by the number of elements. You know what I meen jelly bean LOL LOL
No need to be sorry dude it's that question thing.... |
|
|||
|
Quote:
So, to add on that; would I need a contactor with as many poles as I have elements, or can I double them up? |
![]() |