  #1 (permalink)  
Old 08-11-2007, 12:21 PM
Amateur Metal Finisher
 
Join Date: Jul 2006
Posts: 204
ed_denu is on a distinguished road
Default Wire size?

The oven elements I'm using are going to only pull about 22 Amps(5170 watts). I plan on installing a new 30Amp circuit about 25' from the service panel using 10Ga wire.

Where I am confused is what size wiring do I need for the service cord(from oven to receptacle) and also the hi-temp wire size going to the elements. In looking at various wire size calculators, and based on the amp draw and distance, this oven should only require 14Ga wiring?

Last edited by ed_denu; 08-11-2007 at 12:24 PM.
Reply With Quote
  #2 (permalink)  
Old 08-11-2007, 09:40 PM
nuttyman's Avatar
Metal Finishing Guru
 
Join Date: Sep 2003
Location: Rio Rancho, NM
Posts: 553
nuttyman
Default Re: Wire size?

the service cord should be able to handle the full amperage draw as the load is then divided & sent to each element. if you're using 10 ga. from the service panel u should use the same to feed the oven. the amperage draw per element determines the size wire for each. how many elements are you using? you can use light ga. wire for the elements. for instance this 18 ga is rated for 23 amps. 8240K31 @ McMaster. if you are using to elements they will pull 11 amps each. have you verified their resistance?
__________________
SouthWest Powderworx
Tyler Nutter
5054803934
www.swpowder.com
myspace/swpowder
tyler@swpowder.com
Reply With Quote
  #3 (permalink)  
Old 08-11-2007, 11:43 PM
Experienced Metal Finisher
 
Join Date: Jan 2003
Posts: 321
chromo
Default Re: Wire size?

I agree somewhat, but the length of the run makes a difference in what is required also, plus if you plan to run other loads from the outlets like air compressor and oven both. You would need to run wire heavy enough for both loads and a breaker big enough for both loads, but wire to each load could be much smaller than from breaker box to outlets.

If 25' from breaker box to outlet near oven you may need a heavier wire than just 5' from outlet to oven.
In any case the wire from outlet to oven must support the full load of the oven running at full blast!
If you have figured correct and 14AWG supports the load then go with 12AWG at least.
I always oversize the wire at least one size and under size the breaker for the wire. If a problem happens a 50amp breaker will trip before a 100amp wire burns! A short in a 30-40amp device should still trip a 50amp breaker.
Reply With Quote
  #4 (permalink)  
Old 08-12-2007, 05:53 AM
Amateur Metal Finisher
 
Join Date: Apr 2007
Posts: 90
BottleFed70 is on a distinguished road
Default Re: Wire size?

There's plenty of safty factor built in already with regards to standard wire/breaker load ratings, no need to go overboard.

For the oven power cord, 10ga wire will suffice.
26 amps sounds like 2 x 3000Watt elements. If that's the case, use 14ga high temp wire for the elements.
Reply With Quote
  #5 (permalink)  
Old 08-12-2007, 10:20 AM
Amateur Metal Finisher
 
Join Date: Jul 2006
Posts: 204
ed_denu is on a distinguished road
Default Re: Wire size?

The 30 amp breaker and 10 ga wire to the receptacle will be dedicated to the oven only.

For the oven electronics I plan on using a single 40 amp SSD controlling both 2585 watt elements. I was looking at using the 842 degree wire(8209K17) from McMaster. It's a 14ga wire rated at 55 amps. I guess this is where I get a little confused. Typical 14 ga romex is usually rated at 15 amps while this high temp wire is rated at 55 amps.

Also, this is the wire gauge calculator I have been looking at.

http://www.csgnetwork.com/wiresizecalc.html

If I calculate the total wire run of this setup, it computes that I only need 14 ga wire for the entire run(23 amps, 240 volt, 50 foot maximum length)? Do house wiring circuits always assume a longer distance run, thus the limitations of 15amps/14ga wire, 20amps/12ga wire, etc.
Reply With Quote
  #6 (permalink)  
Old 08-12-2007, 11:36 AM
Amateur Metal Finisher
 
Join Date: Mar 2006
Posts: 137
defed is on a distinguished road
Default Re: Wire size?

i was told by electrical guys that unless the run is long (250' plus) that the standard specs in the code book are fine...ie 30amp 10ga, 20amp 12ga etc.

tho it never hurts to oversize (except to your wallet). not sure about the other ratings that are stated at mcmaster.
Reply With Quote
  #7 (permalink)  
Old 08-14-2007, 09:19 AM
Amateur Metal Finisher
 
Join Date: Jul 2006
Posts: 204
ed_denu is on a distinguished road
Default Re: Wire size?

Thanks everyone for the replies. My question wasn't so much as to the wire size for the outlet as it was for the internal wiring within the oven.

For the outlet my intent is to use 10 ga wire and a 30 amp breaker(per NEC). I'm thinking that within the oven I could use 14 or 12ga hi temp wire. The wire from McMaster is rated 55 amps for 14ga and 75 amps 12 ga(with some de-rating if multiple conductors or within conduit).

From what I have been able to research there is a difference between the requirements for house wiring using the NEC and chassis wiring which is what I believe would apply to wiring within the oven.

Even regular 14 ga wire has a chassis rating around 32 amps from what I've seen in various tables.
Reply With Quote
  #8 (permalink)  
Old 08-15-2007, 12:40 AM
Amateur Metal Finisher
 
Join Date: Apr 2007
Posts: 90
BottleFed70 is on a distinguished road
Default Re: Wire size?

Quote:
Originally Posted by ed_denu View Post
Thanks everyone for the replies. My question wasn't so much as to the wire size for the outlet as it was for the internal wiring within the oven.

For the outlet my intent is to use 10 ga wire and a 30 amp breaker(per NEC). I'm thinking that within the oven I could use 14 or 12ga hi temp wire. The wire from McMaster is rated 55 amps for 14ga and 75 amps 12 ga(with some de-rating if multiple conductors or within conduit).

From what I have been able to research there is a difference between the requirements for house wiring using the NEC and chassis wiring which is what I believe would apply to wiring within the oven.

Even regular 14 ga wire has a chassis rating around 32 amps from what I've seen in various tables.

Careful when looking at those chassis tables, they assume ambient temperature and unbundled wire. Personally, I'd stick to the household wiring code like someone already mentioned.

Usually it takes at leat 8ga wire for 55amps. 50+ amps out of 14ga doesn't make any sense at all.

I'd use the 14ga wire, but run seperate wires for each element. (13amps each).

What's a SSD? Do you mean SSR? If so, make sure that the SSR has a good heatsink. Ask me how I know...
Reply With Quote
  #9 (permalink)  
Old 08-15-2007, 09:20 AM
Amateur Metal Finisher
 
Join Date: Jul 2006
Posts: 204
ed_denu is on a distinguished road
Default Re: Wire size?

Quote:
Originally Posted by BottleFed70 View Post
What's a SSD? Do you mean SSR? If so, make sure that the SSR has a good heatsink. Ask me how I know...
That would be a typo! Should have been SSR. It's rated 40A and I do have a heat sink. I will monitor the SSR temperature when I first start the oven.
Reply With Quote
  #10 (permalink)  
Old 08-15-2007, 12:49 PM
Amateur Metal Finisher
 
Join Date: Jul 2006
Posts: 204
ed_denu is on a distinguished road
Default Re: Wire size?

Quote:
Originally Posted by BottleFed70 View Post
Careful when looking at those chassis tables, they assume ambient temperature and unbundled wire. Personally, I'd stick to the household wiring code like someone already mentioned.
Your right about the wire being rated for ambient temperature, but at around 400 degrees, the multiplier is .82, or still around 45 amps for 14 ga. Placed into conduit would further reduce the rating, but I don't have those numbers handy.

I think one reason the hi temp wire is rated for higher amps is that it is a
"stranded nickel-plated annealed copper conductor with an
insulation of glass-reinforced mica tape covered with a braided fiberglass
jacket". This quote from the McMaster web site.
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

Similar Threads
Thread Thread Starter Forum Replies Last Post
wire spicing Deecoat Oven Building Forum 0 07-27-2006 09:12 PM
Braided wire kingkat Electroplating Questions 1 04-09-2006 04:31 AM
How do I wire up a 220 to my box? Hodges Oven Building Forum 3 10-25-2005 10:38 PM
where to buy aluminum wire jtsuttle Anodizing Questions 1 03-21-2005 03:42 PM
wire rims craigcraig Powder Coating Questions 3 07-03-2004 07:05 PM


All times are GMT -4. The time now is 05:44 PM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.2.0 RC4
Copyright © Caswell Inc.