Default wire and breaker size

The plate on my oven shows kw =14 for 120/240 and 10.8 for 120/208.

What size breaker and wire should I use for the circuit?

Thanks in advance for your help people.
__________________
Randy

Don't just color it, Coat It!

www.collinspowdercoating.com
Reply With Quote
  #2 (permalink)  
Old 03-23-2008, 12:49 AM
Experienced Metal Finisher
 
Join Date: Sep 2005
Location: South Texas
Posts: 326
CarWiz is an unknown quantity at this point
Default Re: wire and breaker size

Watts
------ = Amperes
Volts

14kw (14,000) / 240 = 58.333A

Your circuit should have a 70A rating. The wire size will depend on the length of the run from the supply box. You could use #10 wire for short runs but anything over about 30', I'd go with #8 wire. (Larger depending on length.) As the length increases, the voltage will drop and the amps will rise. You should have no more than 3% drop in voltage in the circuit to meet standards. Larger wire (#8 ) will lower voltage drop. But like I mentioned, it depends on the run. More info is needed to make a wire suggestion.
Reply With Quote
  #3 (permalink)  
Old 03-23-2008, 01:02 AM
Experienced Metal Finisher
 
Join Date: Sep 2005
Location: South Texas
Posts: 326
CarWiz is an unknown quantity at this point
Default Re: wire and breaker size

Added afterthought:
It looks like you may fall into a different category of electrical needs. (Commercial) You may have to run all your wire through conduit and that changes the specs. The second set of numbers (10.8 for 120/208 ) is for 3-phase power. You'll need to be more specific about your setup.
Reply With Quote
  #4 (permalink)  
Old 03-23-2008, 08:49 AM
Amateur Metal Finisher
 
Join Date: Jul 2006
Posts: 191
ed_denu is on a distinguished road
Default Re: wire and breaker size

I think this is bad advice. While a lot of wire size calculators will give the type of numbers suggested, you need to look at the NEC to determine what is allowable.

10ga wire in a residential application cannot exceed 30 amps. A 70 amp breaker for an oven is looking at 4 ga. I believe commercial wire gauges are the same, but may require conduit as noted above.

Last edited by ed_denu; 03-23-2008 at 09:00 AM.
Reply With Quote
  #5 (permalink)  
Old 03-23-2008, 11:41 PM
Newbie
 
Join Date: Mar 2008
Location: Pittsburgh PA
Posts: 3
rcollins is on a distinguished road
Default Re: wire and breaker size

The oven is a household double oven, oven and range on the bottom and a smaller oven were the Microwave would be. Nothing industrial about it. I am going to use it in my garage and want to add a sub panel in the garage to feed the oven and my 5 horse compressor.
__________________
Randy

Don't just color it, Coat It!

www.collinspowdercoating.com
Reply With Quote
  #6 (permalink)  
Old 03-24-2008, 01:30 PM
Amateur Metal Finisher
 
Join Date: Jul 2006
Posts: 191
ed_denu is on a distinguished road
Default Re: wire and breaker size

Randy, If you need to add a subpanel, then I would just get your electrician to look at the oven when you have the garage subpanel put in. A 70 amp feed would normally be hard wired, not something you would plug into a receptacle.
Reply With Quote
  #7 (permalink)  
Old 03-25-2008, 12:31 PM
Amateur Metal Finisher
 
Join Date: Jul 2007
Location: Western WA.
Posts: 58
PhredAre is on a distinguished road
Default Re: wire and breaker size

If this were my project, I would try to determine the size of the Elements(wattage) that are used and wire accordingly. I'm not familiar with this type of oven, but 14,000 watts seems a little much for a oven of this size. Fred
Reply With Quote
  #8 (permalink)  
Old 03-25-2008, 10:21 PM
Experienced Metal Finisher
 
Join Date: Sep 2005
Location: South Texas
Posts: 326
CarWiz is an unknown quantity at this point
Default Re: wire and breaker size

Quote:
Originally Posted by ed_denu View Post
I think this is bad advice.
Ops. You're right about that. Don't know what I was thinking.

I think you're right too Fred. The label is probably maximum draw with all burners going. The oven itself should be much less.
Reply With Quote
  #9 (permalink)  
Old 03-25-2008, 11:06 PM
Newbie
 
Join Date: Mar 2008
Location: Pittsburgh PA
Posts: 3
rcollins is on a distinguished road
Default Re: wire and breaker size

Here is a picture of the oven. I am going to run a 100 amp sub panel in the garage and use a 60 amp breaker with 6 ga wire for the oven.
Attached Thumbnails
wire-breaker-size-garage.jpg  
__________________
Randy

Don't just color it, Coat It!

www.collinspowdercoating.com
Reply With Quote
Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

Similar Threads
Thread Thread Starter Forum Replies Last Post
Tie wire hdway Electroplating Questions 5 03-13-2008 10:24 PM
Titanium wire ken_the_stp Anodizing Questions 5 09-26-2007 08:18 AM
Wire size? ed_denu Oven Building Forum 10 08-15-2007 08:23 PM
what size kit reaper Electroplating Questions 1 12-16-2005 03:07 PM
How do I wire up a 220 to my box? Hodges Oven Building Forum 3 10-25-2005 10:38 PM


All times are GMT -4. The time now is 03:32 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.2.0 RC4
Copyright © Caswell Inc.