The plate on my oven shows kw =14 for 120/240 and 10.8 for 120/208.
What size breaker and wire should I use for the circuit? Thanks in advance for your help people. |
|
|||
|
Watts
------ = Amperes Volts 14kw (14,000) / 240 = 58.333A Your circuit should have a 70A rating. The wire size will depend on the length of the run from the supply box. You could use #10 wire for short runs but anything over about 30', I'd go with #8 wire. (Larger depending on length.) As the length increases, the voltage will drop and the amps will rise. You should have no more than 3% drop in voltage in the circuit to meet standards. Larger wire (#8 ) will lower voltage drop. But like I mentioned, it depends on the run. More info is needed to make a wire suggestion. |
|
|||
|
Added afterthought:
It looks like you may fall into a different category of electrical needs. (Commercial) You may have to run all your wire through conduit and that changes the specs. The second set of numbers (10.8 for 120/208 ) is for 3-phase power. You'll need to be more specific about your setup. |
|
|||
|
I think this is bad advice. While a lot of wire size calculators will give the type of numbers suggested, you need to look at the NEC to determine what is allowable.
10ga wire in a residential application cannot exceed 30 amps. A 70 amp breaker for an oven is looking at 4 ga. I believe commercial wire gauges are the same, but may require conduit as noted above. Last edited by ed_denu; 03-23-2008 at 09:00 AM. |
|
|||
|
The oven is a household double oven, oven and range on the bottom and a smaller oven were the Microwave would be. Nothing industrial about it. I am going to use it in my garage and want to add a sub panel in the garage to feed the oven and my 5 horse compressor.
|
|
|||
|
Randy, If you need to add a subpanel, then I would just get your electrician to look at the oven when you have the garage subpanel put in. A 70 amp feed would normally be hard wired, not something you would plug into a receptacle.
|
|
|||
|
If this were my project, I would try to determine the size of the Elements(wattage) that are used and wire accordingly. I'm not familiar with this type of oven, but 14,000 watts seems a little much for a oven of this size. Fred
|
|
|||
|
Ops. You're right about that. Don't know what I was thinking.
I think you're right too Fred. The label is probably maximum draw with all burners going. The oven itself should be much less. |
|
|||
|
Here is a picture of the oven. I am going to run a 100 amp sub panel in the garage and use a 60 amp breaker with 6 ga wire for the oven.
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Tie wire | hdway | Electroplating Questions | 5 | 03-13-2008 10:24 PM |
| Titanium wire | ken_the_stp | Anodizing Questions | 5 | 09-26-2007 08:18 AM |
| Wire size? | ed_denu | Oven Building Forum | 10 | 08-15-2007 08:23 PM |
| what size kit | reaper | Electroplating Questions | 1 | 12-16-2005 03:07 PM |
| How do I wire up a 220 to my box? | Hodges | Oven Building Forum | 3 | 10-25-2005 10:38 PM |